[Nut-upsdev] Sweex 1000VA UPS (Lakeview Research)

Arjen de Korte nut+devel at de-korte.org
Sun Dec 7 15:26:13 UTC 2008


Citeren Tom Cassimon <tom at cassimon.mine.nu>:

[...]

> 	Checking device (0925/1234) (007/002)
> 	- VendorID: 0925
> 	- ProductID: 1234
> 	- Manufacturer: ?
> 	- Product: UPS USB MON V1.4
> 	- Serial Number: unknown
> 	- Bus: 007
> 	Trying to match device
> 	Device matches

OK, at least the device matching seems to work.

> 	send: (4 bytes) => 01 00 00 30
> 	read: Resource temporarily unavailable
> 	do_command: Resource temporarily unavailable

And from here, that's it. No response at all. Maybe this is because  
the driver expects the query to be sent as a HID_REPORT_TYPE_INPUT  
instead of the HID_REPORT_TYPE_FEATURE that usb->set_report uses.  
Could you try again with the latest version (r1604) from the trunk? If  
that fails, we also have 'lakeview_usb', which might be worth trying  
out.

[...]

> I use the -u root option because the udev system doesn't seem to change the
> permissions of the device.

I know, this udev rules will be generated automatically in the future  
(and the driver is already setup to support that), but this isn't  
activate yet. For now I have modified this too.

Best regards, Arjen
-- 
Please keep list traffic on the list



More information about the Nut-upsdev mailing list