[Nut-upsdev] You lost support of Belkin Universal UPS F6C1100-UNV

Cadence cadence at rogers.com
Sun Oct 3 04:00:18 UTC 2010


Hi.

My Belkin UPS F6C1100-UNV  works fine with megatec_usb version  1.6
(2.4.1). However, it doesn't work with 2.4.2 nor 2.4.3.

# /lib/nut/megatec_usb_old -D -a belkin
Network UPS Tools - Megatec protocol driver 1.6 (2.4.1)
Serial-over-USB transport layer 0.10
debug level is '1'
Starting UPS detection process...
0 out of 5 detection attempts failed (minimum failures: 2).
Cancelling any pending shutdown or battery test.
Megatec protocol UPS detected.
24.0V battery, interval [19.4V, 27.4V].
Done setting up the UPS.



# /lib/nut/megatec_usb -D -a belkin
Network UPS Tools - Megatec protocol driver 1.6 (2.4.3)
Serial-over-USB transport layer 0.10
   0.000000     debug level is '1'
  32.427474     Starting UPS detection process...
  75.263380     ser_get_line: Device detached? (error -1: error sending
control message: Operation not permitted)
  75.646279     Successfully reconnected
 118.177387     ser_get_line: Device detached? (error -1: error sending
control message: Operation not permitted)
 118.562286     Successfully reconnected
 161.087388     ser_get_line: Device detached? (error -1: error sending
control message: Operation not permitted)
 161.470290     Successfully reconnected
 161.470319     Megatec protocol UPS not detected.



Below are the outputs with higher debugging level:

# /lib/nut/megatec_usb_old -DDDDDDDDDDDD -a belkin
Network UPS Tools - Megatec protocol driver 1.6 (2.4.1)
Serial-over-USB transport layer 0.10
send_to_all: SETINFO driver.parameter.port "/dev/ttyS0"
debug level is '12'
Checking device (1D6B/0001) (006/001)
- VendorID: 1d6b
- ProductID: 0001
- Manufacturer: unknown
- Product: unknown
- Serial Number: unknown
- Bus: 006
Trying to match device
Device does not match - skipping
Checking device (1D6B/0001) (005/001)
- VendorID: 1d6b
- ProductID: 0001
- Manufacturer: unknown
- Product: unknown
- Serial Number: unknown
- Bus: 005
Trying to match device
Device does not match - skipping
Checking device (1D6B/0001) (004/001)
- VendorID: 1d6b
- ProductID: 0001
- Manufacturer: unknown
- Product: unknown
- Serial Number: unknown
- Bus: 004
Trying to match device
Device does not match - skipping
Checking device (0665/5161) (003/002)
- VendorID: 0665
- ProductID: 5161
- Manufacturer: Cypress Semiconductor
- Product: USB to Serial
- Serial Number: unknown
- Bus: 003
Trying to match device
Device matches
 none (-110)
DTR=1, RTS=0
Starting UPS detection process...
Asking for UPS information [I]...
 none (-110)
I => FAILED [short read]
I detail: (1 bytes) => 49
Asking for UPS status [Q1]...
 ok
get_data_phoenix: got so far [(121.3 1]
get_data_phoenix: (8 bytes) => 28 31 32 31 2e 33 20 31
 ok
get_data_phoenix: got so far [(121.3 121.6 121]
get_data_phoenix: (16 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 36 20 31
 32 31
 ok
get_data_phoenix: got so far [(121.3 121.6 121.6 017 5]
get_data_phoenix: (24 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 36 20 31
 32 31 2e 36 20 30 31 37 20 35
 ok
get_data_phoenix: got so far [(121.3 121.6 121.6 017 59.9 27.2]
get_data_phoenix: (32 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 36 20 31
 32 31 2e 36 20 30 31 37 20 35 39 2e 39 20 32 37 2e 32
 ok
get_data_phoenix: got so far [(121.3 121.6 121.6 017 59.9 27.2 N/.A 00]
get_data_phoenix: (40 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 36 20 31
 32 31 2e 36 20 30 31 37 20 35 39 2e 39 20 32 37 2e 32 20 4e 2f 2e 41 20 30
 30
 ok
0]t_data_phoenix: got so far [(121.3 121.6 121.6 017 59.9 27.2 N/.A 00001001
get_data_phoenix: (48 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 36 20 31
 32 31 2e 36 20 30 31 37 20 35 39 2e 39 20 32 37 2e 32 20 4e 2f 2e 41 20 30
 30 30 30 31 30 30 31 0d 30
 none (-110)
Q1 => OK [(121.3 121.6 121.6 017 59.9 27.2 N/.A 00001001]
Q1 VALUES => [121.3 121.6 121.6 17.0 59.9 27.2 0.0 00001001]
Asking for UPS status [Q1]...
 none (-110)
 ok
get_data_phoenix: got so far [(121.3 1]
get_data_phoenix: (8 bytes) => 28 31 32 31 2e 33 20 31
 ok
get_data_phoenix: got so far [(121.3 121.3 121]
get_data_phoenix: (16 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31
 ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 5]
get_data_phoenix: (24 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 33 20 30 31 37 20 35
 ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1]
get_data_phoenix: (32 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31
 ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00]
get_data_phoenix: (40 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
 30
 ok
0]t_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00001001
get_data_phoenix: (48 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
 30 30 30 31 30 30 31 0d 30
 none (-110)
Q1 => OK [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00001001]
Q1 VALUES => [121.3 121.3 121.3 17.0 59.9 27.1 0.0 00001001]
Asking for UPS status [Q1]...
 none (-110)
 ok
get_data_phoenix: got so far [(121.3 1]
get_data_phoenix: (8 bytes) => 28 31 32 31 2e 33 20 31
 ok
get_data_phoenix: got so far [(121.3 121.3 121]
get_data_phoenix: (16 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31
 ok
get_data_phoenix: got so far [(121.3 121.3 121.6 017 5]
get_data_phoenix: (24 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 36 20 30 31 37 20 35
 ok
get_data_phoenix: got so far [(121.3 121.3 121.6 017 59.9 27.1]
get_data_phoenix: (32 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 36 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31
 ok
get_data_phoenix: got so far [(121.3 121.3 121.6 017 59.9 27.1 N/.A 00]
get_data_phoenix: (40 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 36 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
 30
 ok
0]t_data_phoenix: got so far [(121.3 121.3 121.6 017 59.9 27.1 N/.A 00001001
get_data_phoenix: (48 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 36 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
 30 30 30 31 30 30 31 0d 30
 none (-110)
Q1 => OK [(121.3 121.3 121.6 017 59.9 27.1 N/.A 00001001]
Q1 VALUES => [121.3 121.3 121.6 17.0 59.9 27.1 0.0 00001001]
Asking for UPS status [Q1]...
 none (-110)
 ok
get_data_phoenix: got so far [(121.3 1]
get_data_phoenix: (8 bytes) => 28 31 32 31 2e 33 20 31
 ok
get_data_phoenix: got so far [(121.3 121.3 121]
get_data_phoenix: (16 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31
 ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 5]
get_data_phoenix: (24 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 33 20 30 31 37 20 35
 ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1]
get_data_phoenix: (32 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31
 ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00]
get_data_phoenix: (40 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
 30
 ok
0]t_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00001001
get_data_phoenix: (48 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
 30 30 30 31 30 30 31 0d 30
 none (-110)
Q1 => OK [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00001001]
Q1 VALUES => [121.3 121.3 121.3 17.0 59.9 27.1 0.0 00001001]
Asking for UPS status [Q1]...
 none (-110)
 ok
get_data_phoenix: got so far [(121.3 1]
get_data_phoenix: (8 bytes) => 28 31 32 31 2e 33 20 31
 ok
get_data_phoenix: got so far [(121.3 121.3 121]
get_data_phoenix: (16 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31
 ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 5]
get_data_phoenix: (24 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 33 20 30 31 37 20 35
 ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1]
get_data_phoenix: (32 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31
 ok
get_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00]
get_data_phoenix: (40 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
 30
 ok
0]t_data_phoenix: got so far [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00001001
get_data_phoenix: (48 bytes) => 28 31 32 31 2e 33 20 31 32 31 2e 33 20 31
 32 31 2e 33 20 30 31 37 20 35 39 2e 39 20 32 37 2e 31 20 4e 2f 2e 41 20 30
 30 30 30 31 30 30 31 0d 30
 none (-110)
Q1 => OK [(121.3 121.3 121.3 017 59.9 27.1 N/.A 00001001]
Q1 VALUES => [121.3 121.3 121.3 17.0 59.9 27.1 0.0 00001001]
0 out of 5 detection attempts failed (minimum failures: 2).
send_to_all: SETINFO ups.type "standby"
Cancelling any pending shutdown or battery test.
Asking for UPS information [I]...
I => FAILED [short read]
I detail: (1 bytes) => 49
send_to_all: SETINFO ups.mfr "unknown"
send_to_all: SETINFO ups.model "unknown"
Megatec protocol UPS detected.
send_to_all: SETINFO ups.serial "unknown"
Parameter [ignoreoff]: [false]
Asking for UPS power ratings [F]...
 ok
get_data_phoenix: got so far [#120.0 0]
get_data_phoenix: (8 bytes) => 23 31 32 30 2e 30 20 30
 ok
get_data_phoenix: got so far [#120.0 006 24.00]
get_data_phoenix: (16 bytes) => 23 31 32 30 2e 30 20 30 30 36 20 32 34 2e
 30 30
 ok
00]_data_phoenix: got so far [#120.0 006 24.00 60.0
get_data_phoenix: (24 bytes) => 23 31 32 30 2e 30 20 30 30 36 20 32 34 2e
 30 30 20 36 30 2e 30 0d 30 30
 none (-110)
F => OK [#120.0 006 24.00 60.0]
F VALUES => [120.0 6.0 24.0 60.0]
send_to_all: SETINFO battery.voltage.nominal "24.0"
send_to_all: SETINFO input.voltage.nominal "120.0"
send_to_all: SETINFO input.frequency.nominal "60.0"
24.0V battery, interval [19.4V, 27.4V].
send_to_all: SETINFO ups.delay.start "2"
send_to_all: SETINFO ups.delay.shutdown "0"
send_to_all: ADDCMD test.battery.start.deep
send_to_all: ADDCMD test.battery.start
send_to_all: ADDCMD test.battery.stop
send_to_all: ADDCMD shutdown.return
send_to_all: ADDCMD shutdown.stayoff
send_to_all: ADDCMD shutdown.stop
send_to_all: ADDCMD load.on
send_to_all: ADDCMD load.off
send_to_all: ADDCMD reset.input.minmax
send_to_all: ADDCMD reset.watchdog
send_to_all: ADDCMD beeper.toggle
Done setting up the UPS.





*************************************************************************************************


# /lib/nut/megatec_usb -DDDDDDDDDDDD -a belkin
Network UPS Tools - Megatec protocol driver 1.6 (2.4.3)
Serial-over-USB transport layer 0.10
   0.000000     send_to_all: SETINFO driver.parameter.port "/dev/ttyS0"
   0.000120     debug level is '12'
   0.372785     Checking device (1D6B/0001) (006/001)
   0.372905     - VendorID: 1d6b
   0.372920     - ProductID: 0001
   0.372932     - Manufacturer: unknown
   0.372945     - Product: unknown
   0.372956     - Serial Number: unknown
   0.372969     - Bus: 006
   0.372980     Trying to match device
   0.372999     Device does not match - skipping
   0.373020     Checking device (1D6B/0001) (005/001)
   0.373062     - VendorID: 1d6b
   0.373074     - ProductID: 0001
   0.373085     - Manufacturer: unknown
   0.373097     - Product: unknown
   0.373108     - Serial Number: unknown
   0.373119     - Bus: 005
   0.373130     Trying to match device
   0.373145     Device does not match - skipping
   0.373162     Checking device (1D6B/0001) (004/001)
   0.373201     - VendorID: 1d6b
   0.373214     - ProductID: 0001
   0.373225     - Manufacturer: unknown
   0.373237     - Product: unknown
   0.373248     - Serial Number: unknown
   0.373260     - Bus: 004
   0.373271     Trying to match device
   0.373285     Device does not match - skipping
   0.373301     Checking device (0665/5161) (003/002)
   0.382882     - VendorID: 0665
   0.382903     - ProductID: 5161
   0.382915     - Manufacturer: Cypress Semiconductor
   0.382927     - Product: USB to Serial
   0.382939     - Serial Number: unknown
   0.382950     - Bus: 003
   0.382961     Trying to match device
   0.382976     Device matches
   1.387897     libusb_get_interrupt: Connection timed out
   1.387921     get_data_phoenix: got so far []
   1.387943     get_data_phoenix: (8 bytes) => 00 00 00 00 00 00 00 00
   2.389105     libusb_get_interrupt: Connection timed out
   2.389159     get_data_phoenix: got so far []
   2.389185     get_data_phoenix: (16 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
   2.389200      00 00
   3.389906     libusb_get_interrupt: Connection timed out
   3.389947     get_data_phoenix: got so far []
   3.389972     get_data_phoenix: (24 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
   3.389992      00 00 00 00 00 00 00 00 00 00
   4.390898     libusb_get_interrupt: Connection timed out
   4.390944     get_data_phoenix: got so far []
   4.390969     get_data_phoenix: (32 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
   4.390993      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
   5.391894     libusb_get_interrupt: Connection timed out
   5.391919     get_data_phoenix: got so far []
   5.391943     get_data_phoenix: (40 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
   5.391971      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
   5.391985      00
   6.392894     libusb_get_interrupt: Connection timed out
   6.392919     get_data_phoenix: got so far []
   6.392942     get_data_phoenix: (48 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
   6.392970      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
   6.392988      00 00 00 00 00 00 00 00 00
   7.393892     libusb_get_interrupt: Connection timed out
   7.393915     get_data_phoenix: got so far []
   7.393936     get_data_phoenix: (56 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
   7.393963      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
   7.393985      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
   8.394897     libusb_get_interrupt: Connection timed out
   8.394928     get_data_phoenix: got so far []
   8.394952     get_data_phoenix: (64 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
   8.394979      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
   8.395006      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
   9.395894     libusb_get_interrupt: Connection timed out
   9.395918     get_data_phoenix: got so far []
   9.395940     get_data_phoenix: (72 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
   9.395967      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
   9.395994      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
   9.396013      00 00 00 00 00 00 00 00
  10.397896     libusb_get_interrupt: Connection timed out
  10.397924     get_data_phoenix: got so far []
  10.397947     get_data_phoenix: (80 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  10.397974      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  10.398000      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  10.398023      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
  11.399896     libusb_get_interrupt: Connection timed out
  11.399924     get_data_phoenix: got so far []
  11.399948     get_data_phoenix: (88 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  11.399976      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  11.400004      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  11.400032      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  12.400906     libusb_get_interrupt: Connection timed out
  12.400942     get_data_phoenix: got so far []
  12.400967     get_data_phoenix: (96 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  12.400994      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  12.401021      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  12.401048      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  12.401065      00 00 00 00 00 00 00
  13.402904     libusb_get_interrupt: Connection timed out
  13.402945     get_data_phoenix: got so far []
  13.402970     get_data_phoenix: (104 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  13.402998      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  13.403026      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  13.403055      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  13.403076      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
  14.403901     libusb_get_interrupt: Connection timed out
  14.403941     get_data_phoenix: got so far []
  14.403966     get_data_phoenix: (112 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  14.403995      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  14.404023      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  14.404051      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  14.404078      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00
  15.404896     libusb_get_interrupt: Connection timed out
  15.404921     get_data_phoenix: got so far []
  15.404944     get_data_phoenix: (120 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  15.404971      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  15.404998      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  15.405025      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  15.405052      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  15.405069      00 00 00 00 00 00
  16.406898     libusb_get_interrupt: Connection timed out
  16.406930     get_data_phoenix: got so far []
  16.406953     get_data_phoenix: (128 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  16.406980      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  16.407006      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  16.407032      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  16.407058      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  16.407079      00 00 00 00 00 00 00 00 00 00 00 00 00 00
  17.407907     libusb_get_interrupt: Connection timed out
  17.407956     get_data_phoenix: got so far []
  17.407981     get_data_phoenix: (136 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  17.408009      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  17.408035      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  17.408062      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  17.408089      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  17.408114      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00
  18.409906     libusb_get_interrupt: Connection timed out
  18.409955     get_data_phoenix: got so far []
  18.409982     get_data_phoenix: (144 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  18.410010      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  18.410038      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  18.410066      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  18.410094      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  18.410121      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  18.410137      00 00 00 00 00
  19.410905     libusb_get_interrupt: Connection timed out
  19.410951     get_data_phoenix: got so far []
  19.410976     get_data_phoenix: (152 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  19.411003      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  19.411029      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  19.411056      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  19.411083      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  19.411109      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  19.411130      00 00 00 00 00 00 00 00 00 00 00 00 00
  20.411908     libusb_get_interrupt: Connection timed out
  20.411959     get_data_phoenix: got so far []
  20.411987     get_data_phoenix: (160 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  20.412013      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  20.412041      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  20.412067      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  20.412094      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  20.412120      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  20.412145      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00
  21.412908     libusb_get_interrupt: Connection timed out
  21.412956     get_data_phoenix: got so far []
  21.412982     get_data_phoenix: (168 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  21.413010      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  21.413036      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  21.413063      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  21.413090      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  21.413116      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  21.413144      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  21.413160      00 00 00 00
  22.413908     libusb_get_interrupt: Connection timed out
  22.413958     get_data_phoenix: got so far []
  22.413983     get_data_phoenix: (176 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  22.414012      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  22.414041      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  22.414068      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  22.414095      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  22.414124      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  22.414151      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  22.414172      00 00 00 00 00 00 00 00 00 00 00 00
  23.414908     libusb_get_interrupt: Connection timed out
  23.414956     get_data_phoenix: got so far []
  23.414983     get_data_phoenix: (184 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  23.415011      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  23.415039      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  23.415066      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  23.415095      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  23.415122      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  23.415150      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  23.415175      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
  24.415906     libusb_get_interrupt: Connection timed out
  24.415956     get_data_phoenix: got so far []
  24.415983     get_data_phoenix: (192 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  24.416011      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  24.416039      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  24.416067      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  24.416094      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  24.416122      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  24.416150      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  24.416177      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  24.416193      00 00 00
  25.417892     libusb_get_interrupt: Connection timed out
  25.417916     get_data_phoenix: got so far []
  25.417939     get_data_phoenix: (200 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  25.417966      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  25.417994      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  25.418020      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  25.418047      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  25.418074      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  25.418101      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  25.418128      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  25.418149      00 00 00 00 00 00 00 00 00 00 00
  26.418899     libusb_get_interrupt: Connection timed out
  26.418934     get_data_phoenix: got so far []
  26.418961     get_data_phoenix: (208 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  26.418989      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  26.419016      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  26.419044      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  26.419071      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  26.419099      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  26.419127      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  26.419155      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  26.419180      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
  27.420901     libusb_get_interrupt: Connection timed out
  27.420930     get_data_phoenix: got so far []
  27.420955     get_data_phoenix: (216 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  27.420984      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  27.421011      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  27.421038      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  27.421067      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  27.421094      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  27.421121      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  27.421149      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  27.421177      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  27.421192      00 00
  28.422897     libusb_get_interrupt: Connection timed out
  28.422925     get_data_phoenix: got so far []
  28.422949     get_data_phoenix: (224 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  28.422978      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  28.423006      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  28.423033      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  28.423061      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  28.423088      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  28.423115      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  28.423143      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  28.423170      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  28.423190      00 00 00 00 00 00 00 00 00 00
  29.424897     libusb_get_interrupt: Connection timed out
  29.424921     get_data_phoenix: got so far []
  29.424944     get_data_phoenix: (232 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  29.424973      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  29.425001      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  29.425028      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  29.425056      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  29.425084      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  29.425112      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  29.425139      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  29.425166      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  29.425191      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
  30.425894     libusb_get_interrupt: Connection timed out
  30.425917     get_data_phoenix: got so far []
  30.425940     get_data_phoenix: (240 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  30.425967      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  30.425994      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  30.426021      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  30.426049      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  30.426075      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  30.426103      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  30.426130      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  30.426157      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  30.426184      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  30.426199      00
  31.426894     libusb_get_interrupt: Connection timed out
  31.426918     get_data_phoenix: got so far []
  31.426941     get_data_phoenix: (248 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  31.426968      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  31.426996      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  31.427023      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  31.427050      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  31.427077      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  31.427104      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  31.427131      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  31.427159      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  31.427186      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  31.427204      00 00 00 00 00 00 00 00 00
  32.427903     libusb_get_interrupt: Connection timed out
  32.427948     get_data_phoenix: got so far []
  32.427975     get_data_phoenix: (256 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  32.428004      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  32.428032      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  32.428060      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  32.428089      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  32.428116      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  32.428145      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  32.428173      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  32.428201      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  32.428230      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00
  32.428254      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
  32.428268     get_data_phoenix: buffer too small
  32.428288     DTR=1, RTS=0
  32.428317     send_to_all: SETINFO device.type "ups"
  32.428336     send_to_all: SETINFO driver.version "2.4.3"
  32.428354     send_to_all: SETINFO driver.version.internal "1.6"
  32.428373     send_to_all: SETINFO driver.name "megatec_usb"
  32.428398     Starting UPS detection process...
  32.428412     Asking for UPS information [I]...
  33.428908     libusb_get_interrupt: Connection timed out
  33.428940     get_data_phoenix: got so far []
  33.428962     get_data_phoenix: (8 bytes) => 00 00 00 00 00 00 00 00
  34.429897     libusb_get_interrupt: Connection timed out
  34.429926     get_data_phoenix: got so far []
  34.429949     get_data_phoenix: (16 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  34.429964      00 00
  35.431895     libusb_get_interrupt: Connection timed out
  35.431919     get_data_phoenix: got so far []
  35.431941     get_data_phoenix: (24 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  35.431961      00 00 00 00 00 00 00 00 00 00
  36.432894     libusb_get_interrupt: Connection timed out
  36.432920     get_data_phoenix: got so far []
  36.432943     get_data_phoenix: (32 bytes) => 00 00 00 00 00 00 00 00
00 00 00 00 00 00
  36.432966      00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
  37.433898     libusb_get_interrupt: Connection timed out




...and so on.







More information about the Nut-upsdev mailing list