[Nut-upsdev] [HCL] Tripp-Lite Omnismart500 supported by tripplite_usb

Matt Schulte gimpyestrada at gmail.com
Mon Feb 13 16:40:41 UTC 2012


Device manufacturer and name:
Tripp-Lite OmniSmart500

upsc output:
matt at backup:/etc$ sudo upsc tripplite
battery.charge: 100
battery.test.status: Battery OK
battery.voltage: 14.56
battery.voltage.nominal: 12
device.mfr: Tripp Lite
device.model: OMNISMART500
device.type: ups
driver.name: tripplite_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.internal: 0.20
input.voltage: 108.60
input.voltage.nominal: 120
output.voltage: 113.0
ups.debug.load_banks: 0
ups.debug.V: 31 30 32 30 58 58 0d '1020XX.'
ups.delay.shutdown: 64
ups.firmware: F0966.A
ups.firmware.aux: protocol 2001
ups.mfr: Tripp Lite
ups.model: OMNISMART500
ups.power.nominal: 500
ups.productid: 0001
ups.status: OL
ups.vendorid: 09ae
matt at backup:/etc$

shutdown sequence testing results:
Not sure exactly what you would like to see here, but after
configuring everything and pulling the plug the system shut down
correctly when the UPS dropped below 20%.

/etc/log/daemon.log:
Feb 13 10:11:47 backup upsmon[12058]: UPS tripplite at localhost battery is low
Feb 13 10:11:47 backup upsd[11649]: Client upsmon at 127.0.0.1 set FSD on UPS [trip
plite]
Feb 13 10:11:47 backup upsmon[12058]: Executing automatic power-fail shutdown
Feb 13 10:11:47 backup upsmon[12058]: Auto logout and shutdown proceeding

link:
http://www.tripplite.com/en/products/model.cfm?txtModelID=21

Matt Schulte



More information about the Nut-upsdev mailing list