[Nut-upsuser] Ablerex MARS

lonely wolf wolfy at nobugconsulting.ro
Sat Apr 22 13:51:14 UTC 2006


Carlos Rodrigues wrote:

>Measuring the voltages just means letting the UPS charge completely
>(until the bundled software says 100%) and then see what value NUT
>reports for "battery.voltage", and then unplugging the UPS from the
>wall until it goes into low battery, and check again the voltage that
>NUT is reporting.
>  
>
Here are the values
- 100% battery charge, status normal:         battery.voltage: 2.3
- 25% battery charge, upsilon reports "batt low", the UPS is beeping, 
shutdown triggered:   battery.voltage: 1.8

full data provided by upsc before shutting down follows:

[root at wolfy ~]# upsc ablerex at localhost
battery.charge: 0.0
battery.voltage: 1.8
battery.voltage.nominal: 96.0
driver.name: megatec
driver.parameter.port: /dev/ttyS0
driver.version: 2.1.0
driver.version.internal: 1.4
input.frequency: 0.0
input.voltage: 0.0
input.voltage.fault: 190.0
output.voltage: 221.3
output.voltage.nominal: 220.0
ups.delay.shutdown: 2
ups.delay.start: 3
ups.load: 49.0
ups.mfr: Ablerex
ups.model: MS3000RT MS02035C
ups.serial: unknown
ups.status: OB LB
ups.temperature: 41.0


Anything else I can help with ?




More information about the Nut-upsuser mailing list