On Wed, Oct 22, 2008 at 4:38 PM, Charles Lepple <clepple at gmail.com> wrote:
> On Tue, Oct 21, 2008 at 10:17 PM, Roman Serbski <mefystofel at gmail.com> wrote:
>> On Tue, Oct 21, 2008 at 7:29 AM, Charles Lepple <clepple at gmail.com> wrote:
>>> On Wed, Oct 1, 2008 at 7:30 AM, Roman Serbski <mefystofel at gmail.com> wrote:
>>>> %tail /var/log/ups.log
>>>> 20081001 170732 NA NA NA [NA] NA NA
>>>> 20081001 171232 NA NA NA [NA] NA NA
>>>> 20081001 171732 NA NA NA [NA] NA NA
>>>
>>> Sorry that this got pushed to the back burner.
>>>
>>> Have you set the nut_upslog_ups variable for the nut_upslog script? If
>>> you don't get any output from upslog, but you see normal stats from
>>> upsc, then upslog could be pointing to the wrong UPS. Here is the top
>>> of that file:
>>>
>>> # Define these nut_upslog* variables in one of these files:
>>> #       /etc/rc.conf
>>> #       /etc/rc.conf.local
>>> #       /etc/rc.conf.d/nut_upslog
>>> #
>>> # DO NOT CHANGE THESE DEFAULT VALUES HERE
>>> #
>>> nut_upslog_enable=${nut_upslog_enable-"NO"}
>>> nut_upslog_prefix=${nut_upslog_prefix-"%%PREFIX%%"}
>>> nut_upslog_logfile=${nut_upslog_logfile-"/var/log/ups.log"}
>>> nut_upslog_interval=${nut_upslog_interval-"300"}
>>> nut_upslog_ups=${nut_upslog_ups-"myups at localhost"}
>>>
>>> For the non-FreeBSD users in the audience, this is not shipped with
>>> the NUT tarball, but rather included in the *BSD ports collection.
>>
>> Exactly. This values should be defined in /etc/rc.conf. Besides adding
>> nut_upslog_enable="YES" one should also add
>> nut_upslog_ups="tripplite at localhost", where "tripplite at localhost" is
>> the name at host you defined in upsmon.conf.
>
> So does upslog work for you now?

Yes Charles, it works now.

Thank you for your time!