[Nut-upsuser] APC Smart-UPS 1000

Kevin bakdong at gmail.com
Sat Jan 22 09:10:01 UTC 2011


on 22/01/2011 15:35 Arjen de Korte wrote:

> Sorry for the confusion. Yes the value hasn't changed, but I didn't 
> expect that to happen. It should however be modifiable through 'upsrw', 
> so that you might be able to set it to a lower value.
> 
> In the usbhid-ups driver, the 'ups.delay.(start|shutdown|reboot)' values 
> are driver variables. They are only send to the UPS when you initiate 
> the corresponding command. However, on the APC it seems to be possible 
> (mandatory) to store them in the UPS itself.
> 
> So try if you can change this value through upsrw to something like 20 
> seconds and lower the 'offdelay' value to 30 seconds.

I don't pretend to understand this fully at the moment, the 
driver.parameter.offdelay is set to 1, as is the ups.delay.shutdown:

# ./clients/upsc apc1500
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2007/07/07
battery.runtime: 5880
battery.runtime.low: 120
battery.temperature: 32.4
battery.type: PbAc
battery.voltage: 27.4
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1000
device.serial: AS0727233122
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 1
driver.parameter.ondelay: 250
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: APC HID 0.95-patched
driver.version.internal: 0.35
input.sensitivity: high
input.voltage: 230.4
output.voltage: 230.4
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 1
ups.delay.start: 250
ups.firmware: 652.13.I
ups.firmware.aux: 7.3
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2007/07/07
ups.model: Smart-UPS 1000
ups.productid: 0002
ups.serial: AS0727233122
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 051d

#./clients/upsrw -s ups.delay.shutdown=30 -u apcmon -p pass123 apc1500
OK

This sets it to 30:

# ./clients/upsc apc1500
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2007/07/07
battery.runtime: 5880
battery.runtime.low: 120
battery.temperature: 32.4
battery.type: PbAc
battery.voltage: 27.4
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1000
device.serial: AS0727233122
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 1
driver.parameter.ondelay: 250
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: APC HID 0.95-patched
driver.version.internal: 0.35
input.sensitivity: high
input.voltage: 230.4
output.voltage: 230.4
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 30
ups.delay.start: 250
ups.firmware: 652.13.I
ups.firmware.aux: 7.3
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2007/07/07
ups.model: Smart-UPS 1000
ups.productid: 0002
ups.serial: AS0727233122
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 051d

but doesn't affect the initial value of ups.timer.shutdown (90) after 
the shutdown.return command:

# ./clients/upscmd -u apcmon -p pass123 apc1500 shutdown.return
OK

# ./clients/upsc apc1500
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2007/07/07
battery.runtime: 5880
battery.runtime.low: 120
battery.temperature: 32.4
battery.type: PbAc
battery.voltage: 27.0
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1000
device.serial: AS0727233122
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 1
driver.parameter.ondelay: 250
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: APC HID 0.95-patched
driver.version.internal: 0.35
input.sensitivity: high
input.voltage: 230.4
output.voltage: 229.6
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 30
ups.delay.start: 250
ups.firmware: 652.13.I
ups.firmware.aux: 7.3
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2007/07/07
ups.model: Smart-UPS 1000
ups.productid: 0002
ups.serial: AS0727233122
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: 82
ups.timer.start: 242
ups.vendorid: 051d




More information about the Nut-upsuser mailing list