[Nut-upsuser] Problem installing NUT on 16.04

Jack McGee jack at greendesk.net
Sat Dec 3 03:23:09 UTC 2016


This is new install on Ubuntu 16.04, using packages from Synaptic,
*Network UPS Tools upsd 2.7.2

I am getting these messages in the terminal:
Broadcast message from nut at amethi (somewhere) (Fri Dec  2 12:33:03 2016):

UPS CyberUPS1 at localhost is unavailable

I am still unclear on where to set when nut shutdowns system.

I see nut-client and nut server are automatically starting from SystemD.

I had problem initially starting:
*
*mythuser at amethi:/etc/nut$ sudo upsdrvctl start
Network UPS Tools - UPS driver controller 2.7.2
Network UPS Tools - Generic HID driver 0.38 (2.7.2)
USB communication driver 0.32
Can't claim USB device [0764:0501]: could not detach kernel driver from 
interface 0: Operation not permitted
Driver failed to start (exit status=1)

But that appeared to be resolved by unplugging USB cable and replugging it.

now:

mythuser at amethi:/usr/share/doc/nut$ sudo upsdrvctl start
[sudo] password for mythuser:
Network UPS Tools - UPS driver controller 2.7.2
Network UPS Tools - Generic HID driver 0.38 (2.7.2)
USB communication driver 0.32
Duplicate driver instance detected! Terminating other driver!
Using subdriver: CyberPower HID 0.3


mythuser at amethi:~$ sudo /lib/nut/usbhid-ups -DD -a CyberUPS1
Network UPS Tools - Generic HID driver 0.38 (2.7.2)
USB communication driver 0.32
    0.000000    debug level is '2'
    0.000222    upsdrv_initups...
    0.129399    Checking device (1D6B/0003) (004/001)
    0.129541    - VendorID: 1d6b
    0.129547    - ProductID: 0003
    0.129549    - Manufacturer: unknown
    0.129550    - Product: unknown
    0.129552    - Serial Number: unknown
    0.129553    - Bus: 004
    0.129555    Trying to match device
    0.129559    Device does not match - skipping
    0.129564    Checking device (046D/C016) (003/007)
    0.129575    - VendorID: 046d
    0.129578    - ProductID: c016
    0.129580    - Manufacturer: unknown
    0.129583    - Product: unknown
    0.129585    - Serial Number: unknown
    0.129587    - Bus: 003
    0.129589    Trying to match device
    0.129597    Device does not match - skipping
    0.129601    Checking device (04F2/0402) (003/006)
    0.129608    - VendorID: 04f2
    0.129611    - ProductID: 0402
    0.129612    - Manufacturer: unknown
    0.129615    - Product: unknown
    0.129617    - Serial Number: unknown
    0.129619    - Bus: 003
    0.129621    Trying to match device
    0.129623    Device does not match - skipping
    0.129626    Checking device (13FD/1240) (003/005)
    0.129633    - VendorID: 13fd
    0.129636    - ProductID: 1240
    0.129637    - Manufacturer: unknown
    0.129638    - Product: unknown
    0.129640    - Serial Number: unknown
    0.129642    - Bus: 003
    0.129645    Trying to match device
    0.129648    Device does not match - skipping
    0.129651    Checking device (10C4/EA60) (003/004)
    0.129658    - VendorID: 10c4
    0.129660    - ProductID: ea60
    0.129663    - Manufacturer: unknown
    0.129665    - Product: unknown
    0.129667    - Serial Number: unknown
    0.129669    - Bus: 003
    0.129671    Trying to match device
    0.129675    Device does not match - skipping
    0.129678    Checking device (0764/0501) (003/003)
    0.130357    - VendorID: 0764
    0.130363    - ProductID: 0501
    0.130366    - Manufacturer: CPS
    0.130368    - Product: CP1500PFCLCD
    0.130370    - Serial Number: 000000000000
    0.130372    - Bus: 003
    0.130374    Trying to match device
    0.130393    Device matches
    0.130400    failed to claim USB device: could not claim interface 0: 
Device or resource busy
    0.130410    detached kernel driver from USB device...
    0.130841    HID descriptor length 439
    0.131461    Report Descriptor size = 439
    0.131526    Using subdriver: CyberPower HID 0.3
    0.131649    Path: UPS.PowerSummary.iProduct, Type: Feature, 
ReportID: 0x01, Offset: 0, Size: 8, Value: 1
    0.131766    Path: UPS.PowerSummary.iSerialNumber, Type: Feature, 
ReportID: 0x02, Offset: 0, Size: 8, Value: 2
    0.131836    Path: UPS.PowerSummary.ff0100d0, Type: Feature, 
ReportID: 0x1b, Offset: 0, Size: 8, Value: 5
    0.131920    Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, 
ReportID: 0x03, Offset: 0, Size: 8, Value: 4
    0.132015    Path: UPS.PowerSummary.iOEMInformation, Type: Feature, 
ReportID: 0x04, Offset: 0, Size: 8, Value: 3
    0.132097    Path: UPS.PowerSummary.Rechargeable, Type: Feature, 
ReportID: 0x05, Offset: 0, Size: 8, Value: 1
    0.132183    Path: UPS.PowerSummary.CapacityMode, Type: Feature, 
ReportID: 0x06, Offset: 0, Size: 8, Value: 2
    0.132283    Path: UPS.PowerSummary.DesignCapacity, Type: Feature, 
ReportID: 0x07, Offset: 0, Size: 8, Value: 100
    0.132288    Path: UPS.PowerSummary.CapacityGranularity1, Type: 
Feature, ReportID: 0x07, Offset: 8, Size: 8, Value: 5
    0.132293    Path: UPS.PowerSummary.CapacityGranularity2, Type: 
Feature, ReportID: 0x07, Offset: 16, Size: 8, Value: 10
    0.132297    Path: UPS.PowerSummary.WarningCapacityLimit, Type: 
Feature, ReportID: 0x07, Offset: 24, Size: 8, Value: 20
    0.132301    Path: UPS.PowerSummary.RemainingCapacityLimit, Type: 
Feature, ReportID: 0x07, Offset: 32, Size: 8, Value: 10
    0.132306    Path: UPS.PowerSummary.FullChargeCapacity, Type: 
Feature, ReportID: 0x07, Offset: 40, Size: 8, Value: 100
    0.132434    Path: UPS.PowerSummary.RemainingCapacity, Type: Input, 
ReportID: 0x08, Offset: 0, Size: 8, Value: 100
    0.132439    Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, 
ReportID: 0x08, Offset: 0, Size: 8, Value: 100
    0.132443    Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, 
ReportID: 0x08, Offset: 8, Size: 16, Value: 3690
    0.132447    Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, 
ReportID: 0x08, Offset: 8, Size: 16, Value: 3690
    0.132450    Path: UPS.PowerSummary.RemainingTimeLimit, Type: Input, 
ReportID: 0x08, Offset: 24, Size: 16, Value: 300
    0.132454    Path: UPS.PowerSummary.RemainingTimeLimit, Type: 
Feature, ReportID: 0x08, Offset: 24, Size: 16, Value: 300
    0.132561    Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, 
ReportID: 0x09, Offset: 0, Size: 8, Value: 24
    0.132643    Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 
0x0a, Offset: 0, Size: 8, Value: 24
    0.132765    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Input, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
    0.132770    Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Input, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
    0.132774    Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Input, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
    0.132778    Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
    0.132782    Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: 
Input, ReportID: 0x0b, Offset: 4, Size: 1, Value: 1
    0.132786    Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, 
ReportID: 0x0b, Offset: 5, Size: 1, Value: 0
    0.132790    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Feature, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
    0.132795    Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Feature, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
    0.132798    Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Feature, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
    0.132803    Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: 
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
    0.132807    Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: 
Feature, ReportID: 0x0b, Offset: 4, Size: 1, Value: 1
    0.132811    Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature, 
ReportID: 0x0b, Offset: 5, Size: 1, Value: 0
    0.132892    Path: UPS.PowerSummary.AudibleAlarmControl, Type: 
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
    0.132896    Path: UPS.PowerSummary.AudibleAlarmControl, Type: Input, 
ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
    0.132974    Path: UPS.PowerSummary.iManufacturer, Type: Feature, 
ReportID: 0x0d, Offset: 0, Size: 8, Value: 3
    0.133070    Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 
0x0e, Offset: 0, Size: 8, Value: 120
    0.133141    Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x0f, 
Offset: 0, Size: 16, Value: 129
    0.133228    Path: UPS.Input.LowVoltageTransfer, Type: Feature, 
ReportID: 0x10, Offset: 0, Size: 16, Value: 88
    0.133233    Path: UPS.Input.LowVoltageTransfer, Type: Input, 
ReportID: 0x10, Offset: 0, Size: 16, Value: 88
    0.133238    Path: UPS.Input.HighVoltageTransfer, Type: Feature, 
ReportID: 0x10, Offset: 16, Size: 16, Value: 139
    0.133242    Path: UPS.Input.HighVoltageTransfer, Type: Input, 
ReportID: 0x10, Offset: 16, Size: 16, Value: 139
    0.133339    Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x12, 
Offset: 0, Size: 16, Value: 137
    0.133409    Path: UPS.Output.PercentLoad, Type: Feature, ReportID: 
0x13, Offset: 0, Size: 8, Value: 14
    0.133493    Path: UPS.Output.Test, Type: Feature, ReportID: 0x14, 
Offset: 0, Size: 8, Value: 6
    0.133497    Path: UPS.Output.Test, Type: Input, ReportID: 0x14, 
Offset: 0, Size: 8, Value: 6
    0.133596    Path: UPS.Output.DelayBeforeShutdown, Type: Feature, 
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
    0.133669    Path: UPS.Output.DelayBeforeStartup, Type: Feature, 
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
    0.133754    Path: UPS.Output.Boost, Type: Feature, ReportID: 0x17, 
Offset: 0, Size: 1, Value: 0
    0.133758    Path: UPS.Output.Overload, Type: Feature, ReportID: 
0x17, Offset: 1, Size: 1, Value: 0
    0.133855    Path: UPS.Output.ConfigActivePower, Type: Feature, 
ReportID: 0x18, Offset: 0, Size: 16, Value: 900
    0.133925    Path: UPS.Output.ff010043, Type: Feature, ReportID: 
0x1a, Offset: 0, Size: 8, Value: 1
    0.133929    Path: UPS.Output.ff010043, Type: Input, ReportID: 0x1a, 
Offset: 0, Size: 8, Value: 1
    0.133941    Report descriptor retrieved (Reportlen = 439)
    0.133943    Found HID device
    0.133946    Detected a UPS: CPS/CP1500PFCLCD
    0.133962    Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, 
ReportID: 0x03, Offset: 0, Size: 8, Value: 4
    0.134170    Path: UPS.PowerSummary.iOEMInformation, Type: Feature, 
ReportID: 0x04, Offset: 0, Size: 8, Value: 3
    0.134400    Path: UPS.PowerSummary.WarningCapacityLimit, Type: 
Feature, ReportID: 0x07, Offset: 24, Size: 8, Value: 20
    0.134407    Path: UPS.PowerSummary.RemainingCapacityLimit, Type: 
Feature, ReportID: 0x07, Offset: 32, Size: 8, Value: 10
    0.134416    Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, 
ReportID: 0x08, Offset: 0, Size: 8, Value: 100
    0.134424    Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, 
ReportID: 0x08, Offset: 8, Size: 16, Value: 3690
    0.134432    Path: UPS.PowerSummary.RemainingTimeLimit, Type: 
Feature, ReportID: 0x08, Offset: 24, Size: 16, Value: 300
    0.134438    Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, 
ReportID: 0x09, Offset: 0, Size: 8, Value: 24
    0.134444    Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 
0x0a, Offset: 0, Size: 8, Value: 24
    0.134450    Path: UPS.Output.PercentLoad, Type: Feature, ReportID: 
0x13, Offset: 0, Size: 8, Value: 14
    0.134456    Path: UPS.PowerSummary.AudibleAlarmControl, Type: 
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
    0.134462    Path: UPS.Output.Test, Type: Feature, ReportID: 0x14, 
Offset: 0, Size: 8, Value: 6
    0.134468    Path: UPS.Output.ConfigActivePower, Type: Feature, 
ReportID: 0x18, Offset: 0, Size: 16, Value: 900
    0.134480    Path: UPS.Output.DelayBeforeStartup, Type: Feature, 
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
    0.134486    Path: UPS.Output.DelayBeforeShutdown, Type: Feature, 
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
    0.134495    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Feature, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
    0.134502    Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Feature, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
    0.134508    Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Feature, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
    0.134514    Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: 
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
    0.134518    Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: 
Feature, ReportID: 0x0b, Offset: 4, Size: 1, Value: 1
    0.134524    Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature, 
ReportID: 0x0b, Offset: 5, Size: 1, Value: 0
    0.134530    Path: UPS.Output.Boost, Type: Feature, ReportID: 0x17, 
Offset: 0, Size: 1, Value: 0
    0.134535    Path: UPS.Output.Overload, Type: Feature, ReportID: 
0x17, Offset: 1, Size: 1, Value: 0
    0.134539    Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 
0x0e, Offset: 0, Size: 8, Value: 120
    0.134545    Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x0f, 
Offset: 0, Size: 16, Value: 129
    0.134552    Path: UPS.Input.LowVoltageTransfer, Type: Feature, 
ReportID: 0x10, Offset: 0, Size: 16, Value: 88
    0.134560    Path: UPS.Input.HighVoltageTransfer, Type: Feature, 
ReportID: 0x10, Offset: 16, Size: 16, Value: 139
    0.134568    Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x12, 
Offset: 0, Size: 16, Value: 137
    0.134575    Path: UPS.Output.Test, Type: Feature, ReportID: 0x14, 
Offset: 0, Size: 8, Value: 6
    0.134579    Path: UPS.Output.Test, Type: Feature, ReportID: 0x14, 
Offset: 0, Size: 8, Value: 6
    0.134585    Path: UPS.Output.Test, Type: Feature, ReportID: 0x14, 
Offset: 0, Size: 8, Value: 6
    0.134590    Path: UPS.Output.DelayBeforeShutdown, Type: Feature, 
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
    0.134596    Path: UPS.Output.DelayBeforeStartup, Type: Feature, 
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
    0.134601    Path: UPS.Output.DelayBeforeShutdown, Type: Feature, 
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
    0.134608    Path: UPS.PowerSummary.AudibleAlarmControl, Type: 
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
    0.134613    Path: UPS.PowerSummary.AudibleAlarmControl, Type: 
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
    0.134618    Path: UPS.PowerSummary.AudibleAlarmControl, Type: 
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
    0.134622    Path: UPS.PowerSummary.AudibleAlarmControl, Type: 
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
    0.134627    Path: UPS.PowerSummary.AudibleAlarmControl, Type: 
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
    0.134638    upsdrv_initinfo...
    0.134642    upsdrv_updateinfo...
    0.142763    Got 6 HID objects...
    0.142771    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Input, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
    0.142775    Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Input, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
    0.142779    Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Input, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
    0.142784    Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
    0.142791    Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: 
Input, ReportID: 0x0b, Offset: 4, Size: 1, Value: 1
    0.142796    Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, 
ReportID: 0x0b, Offset: 5, Size: 1, Value: 0
    0.142799    Quick update...
    0.142805    Path: UPS.Output.DelayBeforeStartup, Type: Feature, 
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
    0.142809    Path: UPS.Output.DelayBeforeShutdown, Type: Feature, 
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
    0.142812    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Feature, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
    0.142816    Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Feature, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
    0.142820    Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Feature, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
    0.142822    Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: 
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
    0.142850    dstate_init: sock /var/run/nut/usbhid-ups-CyberUPS1 open 
on fd 5
    0.142856    upsdrv_updateinfo...
    0.393937    libusb_get_interrupt: Connection timed out
    0.393943    Got 0 HID objects...
    0.393946    Quick update...
    0.393950    Path: UPS.Output.DelayBeforeStartup, Type: Feature, 
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
    0.393954    Path: UPS.Output.DelayBeforeShutdown, Type: Feature, 
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
    0.393959    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Feature, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
    0.393963    Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Feature, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
    0.393966    Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Feature, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
    0.393969    Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: 
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
    2.144632    upsdrv_updateinfo...
    2.150754    Got 6 HID objects...
    2.150764    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Input, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
    2.150769    Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Input, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
    2.150773    Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Input, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
    2.150784    Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
    2.150788    Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: 
Input, ReportID: 0x0b, Offset: 4, Size: 1, Value: 1
    2.150793    Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, 
ReportID: 0x0b, Offset: 5, Size: 1, Value: 0
    2.150800    Quick update...
    2.150893    Path: UPS.Output.DelayBeforeStartup, Type: Feature, 
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
    2.150989    Path: UPS.Output.DelayBeforeShutdown, Type: Feature, 
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
    2.150997    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Feature, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
    2.151000    Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Feature, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
    2.151003    Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Feature, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
    2.151006    Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: 
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
    4.146648    upsdrv_updateinfo...
    4.150744    Got 3 HID objects...
    4.150755    Path: UPS.PowerSummary.RemainingCapacity, Type: Input, 
ReportID: 0x08, Offset: 0, Size: 8, Value: 100
    4.150763    Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, 
ReportID: 0x08, Offset: 8, Size: 16, Value: 3720
    4.150775    Path: UPS.PowerSummary.RemainingTimeLimit, Type: Input, 
ReportID: 0x08, Offset: 24, Size: 16, Value: 300
    4.150779    Quick update...
    4.150873    Path: UPS.Output.DelayBeforeStartup, Type: Feature, 
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
    4.150968    Path: UPS.Output.DelayBeforeShutdown, Type: Feature, 
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
    4.151062    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Feature, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
    4.151069    Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Feature, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
    4.151072    Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Feature, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
    4.151075    Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: 
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
    6.148665    upsdrv_updateinfo...
    6.150731    Got 6 HID objects...
    6.150741    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Input, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
    6.150746    Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Input, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
    6.150751    Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Input, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
    6.150758    Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
    6.150766    Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: 
Input, ReportID: 0x0b, Offset: 4, Size: 1, Value: 1
    6.150771    Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, 
ReportID: 0x0b, Offset: 5, Size: 1, Value: 0
    6.150776    Quick update...
    6.150895    Path: UPS.Output.DelayBeforeStartup, Type: Feature, 
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
    6.150992    Path: UPS.Output.DelayBeforeShutdown, Type: Feature, 
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
    6.150999    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Feature, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
    6.151002    Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Feature, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
    6.151005    Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Feature, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
    6.151008    Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: 
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
    8.150686    upsdrv_updateinfo...

*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20161202/a4fdefc6/attachment-0001.html>


More information about the Nut-upsuser mailing list