Hi Daniel,<br><br>sorry for the time taken to provide you an answer, but there it is :)<br><br>There is a data (HID: UPS.PowerSummary.PresentStatus.Switchable) that wasn't mapped in NUT.<br>This data allows to send shutdown order to the UPS, and is equivalent to what you have on the LCD screen of the UPS.<br>
<br>I've not seen this before because this data is enabled by default...<br><br>The fix is both attached (limited to the code) and committed to the trunk r3717:<br><a href="http://trac.networkupstools.org/projects/nut/changeset/3717">http://trac.networkupstools.org/projects/nut/changeset/3717</a><br>
<br>Once applied, check with upsc that "ups.shutdown" is set to "enabled".<br>Otherwise, use:<br># upsrw -u <user> -p <password> -s ups.shutdown="enabled" <device name><br><br>
You can then test it using "upsmon -c fsd" if you have protected loads, or simply with:<br># upscmd  -u <user> -p <password>  <device name> shutdown.return<br><br>Can you please confirm back that the issue is closed on your side?<br>