<br><div class="gmail_quote">2012/9/7 Fabio Cecamore <span dir="ltr"><<a href="mailto:ceca_89@hotmail.com" target="_blank">ceca_89@hotmail.com</a>></span><br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
I've done what you said but now..<br>
<br>
root@ProLiant:/home/fabio# upsrw -u admin -p mypass -s ups.delay.shutdown=180 ups<br>
Unexpected response from upsd: ERR READONLY<br>
root@ProLiant:/home/fabio#<br>
<br>
I hope this not mean this variable is readonly..<br></blockquote><div><br>hem Fabio, I'm sure you're actually kiding with your comment ;)<br>To get the list of variables that can be set, use "upsrw <ups name>".<br>
You will see that ups.delay.shutdown is not present.<br> <br>What you probably want is to configure the delay before powering off the UPS, at the end of the shutdown sequence.<br>Just use "offdelay = <value>" in ups.conf, as described in the blazer manpage:<br>
<a href="http://www.networkupstools.org/docs/man/blazer.html">http://www.networkupstools.org/docs/man/blazer.html</a><br><br>cheers,<br>Arnaud<br></div></div>-- <br>Linux / Unix / Opensource Engineering Expert - Eaton - <a href="http://opensource.eaton.com" target="_blank">http://opensource.eaton.com</a><br>
Network UPS Tools (NUT) Project Leader - <a href="http://www.networkupstools.org" target="_blank">http://www.networkupstools.org</a><br>Debian Developer - <a href="http://www.debian.org" target="_blank">http://www.debian.org</a><br>
Free Software Developer - <a href="http://arnaud.quette.fr" target="_blank">http://arnaud.quette.fr</a><br><br>