Michal, Kastus, Jack,<br><br>I have a similar request sitting in the Features requests for years:<br><a href="https://alioth.debian.org/tracker/index.php?func=detail&aid=304645&group_id=30602&atid=411545">https://alioth.debian.org/tracker/index.php?func=detail&aid=304645&group_id=30602&atid=411545</a><br>
<a href="http://lists.alioth.debian.org/pipermail/nut-upsdev/2006-June/000938.html">http://lists.alioth.debian.org/pipermail/nut-upsdev/2006-June/000938.html</a><br><br>would you please unite your efforts and bring a patch for NUT FAQ (or the driver(s))?<br>
<br>thanks a lot!<br>Arnaud<br>-- <br>NUT (Network UPS Tools) Project Leader - <a href="http://www.networkupstools.org" target="_blank">http://www.networkupstools.org</a><br>Debian Developer - <a href="http://www.debian.org" target="_blank">http://www.debian.org</a><br>
Free Software Developer - <a href="http://arnaud.quette.fr" target="_blank">http://arnaud.quette.fr</a><br><br><div class="gmail_quote">2012/11/11 Kastus Shchuka <span dir="ltr"><<a href="mailto:ks-nut@tprfct.net" target="_blank">ks-nut@tprfct.net</a>></span><br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div class="im">On Sun, Nov 11, 2012 at 07:21:35AM -0800, JS wrote:<br>
> I followed this procedure (charging the battery fully, letting it drain off a token load while UPS is grounded on a surge protector) but it did not help.<br>
><br>
> Perhaps I missed something running this procedure; if anyone has suggestions for solving this they'd be greatly appreciated.<br>
<br>
</div>I've been in the same situation after replacing the battery in SC620I model.<br>
<br>
Then I found <a href="http://old.nabble.com/SmartUPS-and-new-battery-td20678966.html" target="_blank">http://old.nabble.com/SmartUPS-and-new-battery-td20678966.html</a><br>
and followed the procedure:<br>
<br>
1. Shutdown the apcupsd daemon.<br>
2. Run apctest<br>
3. Choose option 6 to enter terminal mode<br>
4. Enter Y (UPS should respond SM)<br>
5. Enter 1 (one, not el; wait 4 seconds)<br>
6. Enter 1 (one, not el; UPS should respond PROG)<br>
7. Enter 0 (zero, not oh; UPS should respond with current constant)<br>
8. Enter + (plus) or - (minus) to increment/decrement the value<br>
9. Enter R to reprogram constant value (UPS should respond Bye)<br>
10. Enter Y (UPS should respond SM)<br>
11. Enter 0 (zero, not oh; UPS should respond with the new constant)<br>
12. Enter Esc to exit terminal mode<br>
13. Choose option 7 to exit apctest.<br>
<br>
The value to store in the register 0 differs by the model. There is a table<br>
posted in the middle of the thread. I hope your model is listed there.<br>
If you cannot find your model, you may want to try experimenting with different<br>
values.<br>
<br>
In my case, after updating register 0, my UPS is back to 42 min runtime.<br>
<br>
Hope this helps.<br>
<br>
Kastus<br>
<br>
</blockquote></div>