<br><div class="gmail_quote">2012/11/26 Franck <span dir="ltr"><<a href="mailto:franck@secretfatty.net" target="_blank">franck@secretfatty.net</a>></span><br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div class="im">On 2012-11-26 18:39, Arnaud Quette wrote:<br>
</div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Hi Franck<br>
<br>
2012/11/23 Franck <<a href="mailto:franck@secretfatty.net" target="_blank">franck@secretfatty.net</a> [3]><br>
<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Subject: [Nut-upsuser] CyberPower DX600E wont switch up after<div class="im"><br>
power<br>
        is back<br>
Message-ID: <<a href="mailto:3c530815d1ea602efdfec0d67eb1e0b1@secretfatty.net" target="_blank">3c530815d1ea602efdfec0d67eb1e<u></u>0b1@secretfatty.net</a><br></div>
[1]><div class="im"><br>
Content-Type: text/plain; charset=UTF-8; format=flowed<br>
<br>
Hello<br>
I have an issue with an CyberPower DX600E,<br></div>
it doesnt switch up when the power is back; after it has been<div class="im"><br>
unloaded;<br>
is it because of one of those variables ?<br>
regards<br>
Franck<br>
<br>
#upsc myups<br>
battery.charge: 100<br>
battery.charge.low: 10<br>
battery.charge.warning: 20<br>
battery.mfr.date: CPS<br>
battery.runtime: 1380<br>
battery.runtime.low: 300<br>
battery.type: PbAcid<br>
battery.voltage: 4.7<br>
battery.voltage.nominal: 12<br>
device.mfr: CPS<br>
device.model: DX600E<br>
device.type: ups<br>
</div><a href="http://driver.name" target="_blank">driver.name</a> [2]: usbhid-ups<div><div class="h5"><br>
driver.parameter.pollfreq: 30<br>
driver.parameter.pollinterval: 2<br>
driver.parameter.port: auto<br>
driver.version: 2.4.3<br>
driver.version.data: CyberPower HID 0.3<br>
driver.version.internal: 0.34<br>
input.transfer.high: 0<br>
input.transfer.low: 0<br>
input.voltage: 230.0<br>
input.voltage.nominal: 230<br>
output.voltage: 238.0<br>
ups.beeper.status: enabled<br>
ups.delay.shutdown: 20<br>
ups.delay.start: 30<br>
ups.load: 31<br>
ups.mfr: CPS<br>
ups.model: DX600E<br>
ups.productid: 0501<br>
ups.realpower.nominal: 360<br>
ups.status: OL<br>
ups.timer.shutdown: -60<br>
ups.timer.start: 0<br>
ups.vendorid: 0764<br>
</div></div></blockquote><div><div class="h5">
<br>
Am i suppose to run a "shutdown.return" command ?<br>
<br>
Does it make sense to do it in the script triggering (for example<br>
when receiving "low battery" ?<br>
</div></div></blockquote><div><div class="h5">
<br>
depending on your exact OS / distros, this should be handled by NUT<br>
initscripts and probably the halt one.<br>
 what is yours?<br>
<br>
</div></div></blockquote>
<br>
Thanks for your reply Arnaud;<br>
I have a debian squeeze.<br>
</blockquote></div><br>looking again at your upsc output, I suspect more an issue with the UPS than with Squeeze.<br><br>a good test would be to:<br>- remove your PC from the UPS,<br>- stop NUT after the reboot,<br>- restart the driver in debug more (/lib/nut/usbhid-ups -DDDDD myups) and upsd (simply type "upsd") in another term<br>
- then execute "upscmd -u ... -p ... myups shutdown.return"<br>- leave it half a minute, then Ctrl+C in the driver term.<br>and send back the driver output, in compressed form.<br>you can then restart everything as usual...<br>
<br>I'd like to see how the data behind "ups.timer.shutdown" and "ups.timer.start" behave.<br><br>cheers,<br clear="all">Arnaud<br>-- <br>NUT (Network UPS Tools) Project Leader - <a href="http://www.networkupstools.org" target="_blank">http://www.networkupstools.org</a><br>
Debian Developer - <a href="http://www.debian.org" target="_blank">http://www.debian.org</a><br>Free Software Developer - <a href="http://arnaud.quette.fr" target="_blank">http://arnaud.quette.fr</a><br><br>