<DIV><FONT size=2><FONT size=3>Good Day Roger<BR><BR>AA. notice that
during the test, you have little or no load, since despite <BR>being in state
OB<BR> DISCHRG the battery.charge is still 100. It's best to perform
such tests <BR>with a dummy load<BR>such as a table lamp and an old fashioned
incandescent 100 watt bulb.<BR><BR>==> Yes. I got it and try to ascend load
as below results<BR><BR>dinow-All-Series:~# upsc pcmups<BR>Init SSL without
certificate database<BR>battery.charge: 32<BR>battery.charge.low:
10<BR>battery.charge.warning: 30<BR>battery.date: 2010/12/20<BR>battery.runtime:
256<BR>battery.type: PbAc<BR>device.mfr: POWERCOM Co.,LTD<BR>device.model: HID
UPS Battery<BR>device.serial: 004-0D9F-000<BR>device.type: ups<BR>driver.name:
usbhid-ups<BR>driver.parameter.pollfreq: 30<BR>driver.parameter.pollinterval:
2<BR>driver.parameter.port: auto<BR>driver.version:
2.7.1<BR>driver.version.data: PowerCOM HID 0.4<BR>driver.version.internal:
0.38<BR>input.frequency: 0.0<BR>input.voltage: 0.0<BR>output.frequency:
60.0<BR>output.voltage: 110.0<BR>ups.beeper.status: disabled<BR>ups.date:
2010/12/20<BR>ups.delay.shutdown: 20<BR>ups.delay.start: 60<BR>ups.load:
58<BR>ups.mfr: POWERCOM Co.,LTD<BR>ups.model: HID UPS Battery<BR>ups.productid:
0004<BR>ups.serial: 004-0D9F-000<BR>ups.status: OB DISCHRG
TRIM<BR>ups.test.result: Done and passed<BR>ups.timer.shutdown:
169<BR>ups.timer.start: 755760<BR>ups.vendorid:
0d9f<BR><BR>----------------------------------------------------------------------------------------<BR>BB.
I wonder where the ups.delay.start: 60 comes from. The NUT default
<BR>value<BR> is 30 secs, and you do not change the value in
ups.conf.<BR><BR>==> I tried below set-command but it react
fail<BR><BR>dinow-All-Series:~# upsrw -s "ups.delay.shutdown"="30" -u pcmups
<BR></FONT><A href="mailto:pcmups@localhost"><FONT
size=3>pcmups@localhost</FONT></A><BR><FONT size=3>Password:<BR>Unexpected
response from upsd: ERR ACCESS-DENIED<BR><BR>==> Are there any behaviors that
I should confirm
?<BR><BR><BR><BR>----------------------------------------------------------------------------------------<BR>CC.
Does a Ubuntu user with no xterm window open see the message as part of
<BR>the<BR><BR>==> The root and remote user(ssh-putty) get the broadcasting
message all <BR>from
terminal-window<BR><BR><BR><BR>----------------------------------------------------------------------------------------<BR>DD.
I have tried below commands and the ups actually works (Battery test and
<BR>Beeper ON/OFF)<BR><BR>dinow-All-Series:~# upscmd -l pcmups<BR>Instant
commands supported on UPS [pcmups]:<BR><BR>beeper.disable - Disable the UPS
beeper<BR>beeper.enable - Enable the UPS beeper<BR>beeper.toggle - Toggle the
UPS beeper<BR>load.on - Turn on the load immediately<BR>load.on.delay - Turn on
the load with a delay (seconds)<BR>shutdown.return - Turn off the load and
return when power is back<BR>shutdown.stayoff - Turn off the load and remain
off<BR>test.battery.start.quick - Start a quick battery
test<BR><BR><BR>dinow-All-Series:~# upscmd pcmups
test.battery.start.quick<BR>Username (root): pcmups<BR>Password:<BR>OK<BR>==>
The ups run battery mode<BR><BR><BR>dinow-All-Series:~# upscmd pcmups
beeper.disable<BR>Username (root): pcmups<BR>Password:<BR>OK<BR>==> The ups
turn off it beeper when its on battery mode<BR><BR><BR>==> However, I command
center 5 (load.on / delay / shutdown return / stay <BR>off) but no any reaction
occur<BR><BR><BR><BR><BR><BR>If you have any questions, please don't hesitate to
inform us.<BR>Sincerely yours, May. 17th<BR>Dinow Hsieh<BR>----- Original
Message ----- <BR>From: "Roger Price" <</FONT><A
href="mailto:roger@rogerprice.org"><FONT
size=3>roger@rogerprice.org</FONT></A><FONT size=3>><BR>To: "nut-upsuser
Mailing List" <</FONT><A
href="mailto:nut-upsuser@lists.alioth.debian.org"><FONT
size=3>nut-upsuser@lists.alioth.debian.org</FONT></A><FONT size=3>><BR>Sent:
Tuesday, May 16, 2017 5:24 PM<BR>Subject: Re: [Nut-upsuser] Fw: [Nut-upsdev]
POWERCOM-UPS-USB : UPS Shutdown<BR><BR><BR>> On Tue, 16 May 2017, Dinow Hsieh
wrote:<BR>><BR>>> BB. Could you show us the output of command "upsc
pcmups"?<BR>>><BR>>> ==> Yes. Below 2 mode were the outputs of
command "upsc pcmups"<BR>>><BR>>> battery.charge: 100<BR>>>
battery.charge.low: 10<BR>>> battery.charge.warning: 30<BR>>>
battery.date: 2010/12/20<BR>> ...<BR>>> ups.date:
2010/12/20<BR>>> ups.load: 4<BR>> ...<BR>>> ups.status: OB
DISCHRG<BR>><BR>> Is this battery really 6.5 years old? Is this part
of the problem? One<BR>> would not expect such a battery to support any
load. I notice that during<BR>> the test, you have little or no load,
since despite being in state OB<BR>> DISCHRG the battery.charge is still
100. It's best to perform such tests<BR>> with a dummy load such as a
table lamp and an old fashioned incandescent<BR>> 100 watt
bulb.<BR>><BR>>> ups.delay.shutdown: 20<BR>>> ups.delay.start:
60<BR>><BR>> I wonder where the ups.delay.start: 60 comes from. The
NUT default value<BR>> is 30 secs, and you do not change the value in
ups.conf.<BR>><BR>>> DD. Does wall successfully notify the users on an
Ubuntu system? If you<BR>>> type<BR>>><BR>>> echo "Hello from
wall" | wall<BR>>><BR>>> do the users of Gnome, KDE, LXDE, LightDM
etc see the message?<BR>>><BR>>> ==> Yes. I used the putty and
got below 3 messages<BR>>> (Battery Power / Power Resotre / and type
commands directly)<BR>>><BR>>><BR>>> D3. Broadcast Message
from dinow-Al<BR>>> (/dev/pts/0) at 11:02 ...<BR>>><BR>>>
Hello from wall<BR>><BR>> I'm guessing that this output is in an xterm
window or something similar.<BR>> It shows that wall is working but does not
show that the wall->Gnome,<BR>> wall->KDE, wall->LXDE,
wall->LightDM interfaces are working. Does a<BR>> Ubuntu user with
no xterm window open see the message as part of the<BR>> system
notifications?<BR>><BR>>
Roger<BR><BR><BR>--------------------------------------------------------------------------------<BR><BR><BR>>
_______________________________________________<BR>> Nut-upsuser mailing
list<BR>> </FONT><A href="mailto:Nut-upsuser@lists.alioth.debian.org"><FONT
size=3>Nut-upsuser@lists.alioth.debian.org</FONT></A><BR><FONT size=3>>
</FONT><A
href="http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser"><FONT
size=3>http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser</FONT></A><FONT
size=3> </FONT><BR></FONT></DIV></BODY></HTML>