[Nut-upsdev] Some question about megatec vs. powercom

Carlos Rodrigues carlos.efr at mail.telepac.pt
Wed Jan 23 17:42:15 UTC 2008


On Jan 23, 2008 3:49 PM, Ekkehard Gehm <gehm at physik.tu-berlin.de> wrote:
> Megatec protocol UPS detected [UPS Model 6K Ver Y1.3].
> This UPS has an unsupported combination of battery voltage/number of batteries. The "battery.charge" value will be bogus.
>
> So I would like to try adding this feature. But actually I don't have any idea where to start :-)

If you have a recent enough version of NUT, megatec supports a
parameter "battvolts" where you can specify the battery voltage when
the UPS is fully charged, and the voltage when the UPS is discharged.

You can run "megatec -DDD yourups" while powering a lightbulb or
another non-important device, disconnect from the wall and let the UPS
drain the battery until it shuts itself down. Then send me the output
and I'll help you find the values from it.

-- 
Carlos Rodrigues



More information about the Nut-upsdev mailing list