Hi Robert,

Liebert's Multilink is the only original source of information, so if 
Multilink doesn't do it, there is no known command. If Multilink does 
offer that function, you will still need to sniff the protocol to find 
the commands it uses - only then will it be possible to implement this 
feature in NUT.

With regard to the patches so far, we have:
1. reply[] byte swap patch
2. All the other instances of byte swapping reply[] patch
3. "ups.firmware" register location patch

In between this, there was Spiros's observation that the the Liebert NXe 
doesn't return some of the text strings that the GXT2 returns. Assuming 
the driver is otherwise compatible (is it??), the most compatible fix is 
to get the strings separately and only make some of them an error condition.

Also, the NXe has two serial ports, one 2400 baud (same as the GXT2), 
which is disabled when using the ethernet option and another at 9600 
baud. The NUT driver assumes 2400 baud. To find how to implement this, 
will need to find an example NUT driver that uses differing serial baud 
rates, any suggestions?


Richard

+--                               --+
|  Biological Sciences, Room 231    |
|  http://www.csc.liv.ac.uk/~greg   |
+--                               --+

Robert Jobbagy wrote:
> Hi guys,
> 
> I would like switch to battery from online my ups.
> Is it possible?exist something command that I do it?
> 
> Thanks your help.
> 
> 2010/4/9 Robert Jobbagy <jobbagy.robert at gmail.com 
> <mailto:jobbagy.robert at gmail.com>>
> 
>     Hi Arjen!
> 
>     This is the my last patch to Liebert GXT2 driver.
> 
> 
>     ---------- Forwarded message ----------
>     From: *Robert Jobbagy* <jobbagy.robert at gmail.com
>     <mailto:jobbagy.robert at gmail.com>>
>     Date: 2010/4/7
>     Subject: Re: [Nut-upsdev] Liebert GXT2 NUT driver
>     To: NUT Developers <nut-upsdev at lists.alioth.debian.org
>     <mailto:nut-upsdev at lists.alioth.debian.org>>
> 
> 
>     Hi Guys,
> 
>     I tested this driver and I found a bug,
> 
>     The wrong output:
> 
>     device.serial: GXT2MR15D
>     ups.firmware: 12OCT04
>     ups.mfr.date: 0428100126AF041
>     ups.serial: GXT2MR15D
> 
>     The right output:
> 
>     device.serial: 0428100126AF041
>     ups.firmware: GXT2MR15D
>     ups.mfr.date: 12OCT04
>     ups.serial: 0428100126AF041
> 
>     I fix it and attached the patch.
> 
>     2010/4/7 Spiros Ioannou <sivann at gmail.com <mailto:sivann at gmail.com>>
> 
>         On the battery issue:
>         I did some tests:
>         BATTERY_CAPACITY is always 94%, no matter its charge, probably
>         indicating its decay.
>         BATTERY_CHARGED is always NO for me
>         BATTERY_CURRENT does actually indicate when battery is charging
>         or discharging. In the case of discharging (ups on battery) a
>         negative value is indicated.
>         The correct value  can be calculated as follows:
> 
>          float f;
>          f=(signed short int)(256*H+L)/(float)100; //100 is the divider
>         to convert value to Amperes.
> 
>         The actual value of BATTERY_CURRENT in Amperes need to be
>         divided by 100:
>         *CHARGING:*
>         # ./upsesp2 /dev/ttyS0  BATTERY_CURRENT         
>         SendingM: 001,095,002,001,003,09C      
>         BATTERY_CURRENT,bit/divider:100
>         READ    : 001,095,004,001,003, 001,056 (001 086), 0F5  (returned
>         values H,L are decimal 001 086)
>         BATTERY_CURRENT: 3.4
> 
>         *DISCHARGING (on battery)*
>         # ./upsesp2 /dev/ttyS0  BATTERY_CURRENT
>         SendingM: 001,095,002,001,003,09C      
>         BATTERY_CURRENT,bit/divider:100
>         READ    : 001,095,004,001,003, 0FC,020 (252 032), 0BA
>         BATTERY_CURRENT: -9.9
> 
>         -9.9 comes from (255-252)*256 + (255-032) or by casting to
>         signed short int which does the same.
> 
>         After the power comes back on, between discharging and charging
>         there is a period of no battery current (0 Amp) for a few seconds.
> 
>         -S
> 
>         On Tue, Apr 6, 2010 at 9:12 PM, Spiros Ioannou <sivann at gmail.com
>         <mailto:sivann at gmail.com>> wrote:
> 
>             Hi,
>             I managed to find another Liebert UPS, this time a Liebert
>             NXe 20KVA unit, so I can help with the driver again.
>             This one has 2 serial ports, one gets disabled if you
>             connect the ethernet module. The other port is @9600bps. The
>             9600 is the one I use.
> 
>             I applied Richard's patch with the bit correction, and tried
>             the driver (after changing the bitrate), but it failed at
>             startup because Liebert NXe doesn't provide its Serial
>             Number. It seems when trying to read the initial UPS
>             model,SN etc, the UPS replies an invalid 5-byte reply
>             instead of the usual 8-byte one. I attach a debug output
>             (hex)  from my upsesp2.c for comparison. Look at line 109 of
>             dbg_hex.txt.
> 
>             The solution is to replace        
>                     for (i = 0; i < 37; i++) {
>             with
>                     for (i = 0; i < 15; i++) {
> 
>             to just check for MODEL_NAME
> 
>             As for the CHARGED, it seems that in my case the battery
>             BATTERY_CHARGED is always NO perhaps because the UPS uses a
>             percentage battery charge indicator (BATTERY_CAPACITY). I'm
>             not sure I follow your logic with ANDing with the OL flag.
>             The Charging could probably be deducted from the
>             BATTERY_CURRENT value.This could be negative if the battery
>             is charging, but I cannot test it right now.
> 
>             ./liebertgxt2 -a nxe -DD
>             Network UPS Tools - Liebert GXT2 serial UPS driver 0.02
>             (2.4.3-2420)
>             Warning: This is an experimental driver.
>             Some features may not function correctly.
> 
>                0.000000     debug level is '2'
>                0.000737     send: (6 bytes) => 01 88 02 01 04 90
>                0.072087     read: (8 bytes) => 01 88 04 01 04 69 4c 47
>                0.072216     send: (6 bytes) => 01 88 02 01 05 91
>                0.136206     read: (8 bytes) => 01 88 04 01 05 62 65 5a
>                0.136343     send: (6 bytes) => 01 88 02 01 06 92
>                0.202086     read: (8 bytes) => 01 88 04 01 06 72 65 6b
>                0.202209     send: (6 bytes) => 01 88 02 01 07 93
>                0.266083     read: (8 bytes) => 01 88 04 01 07 20 74 29
>                0.266205     send: (6 bytes) => 01 88 02 01 08 94
>                0.328099     read: (8 bytes) => 01 88 04 01 08 58 4e 3c
>                0.328222     send: (6 bytes) => 01 88 02 01 09 95
>                0.402090     read: (8 bytes) => 01 88 04 01 09 00 20 b7
>                0.402212     send: (6 bytes) => 01 88 02 01 0a 96
>                0.468096     read: (8 bytes) => 01 88 04 01 0a 00 00 98
>                0.468220     send: (6 bytes) => 01 88 02 01 0b 97
>                0.559082     read: (8 bytes) => 01 88 04 01 0b 00 00 99
>                0.559205     send: (6 bytes) => 01 88 02 01 0c 98
>                0.623082     read: (8 bytes) => 01 88 04 01 0c 00 00 9a
>                0.623204     send: (6 bytes) => 01 88 02 01 0d 99
>                0.687179     read: (8 bytes) => 01 88 04 01 0d 00 00 9b
>                0.687316     send: (6 bytes) => 01 88 02 01 0e 9a
>                0.753149     read: (8 bytes) => 01 88 04 01 0e 00 00 9c
>                0.753285     send: (6 bytes) => 01 88 02 01 0f 9b
>                0.818205     read: (8 bytes) => 01 88 04 01 0f 00 00 9d
>                0.818342     send: (6 bytes) => 01 88 02 01 10 9c
>                0.880087     read: (8 bytes) => 01 88 04 01 10 00 00 9e
>                0.880210     send: (6 bytes) => 01 88 02 01 11 9d
>                0.972080     read: (8 bytes) => 01 88 04 01 11 00 00 9f
>                0.972203     send: (6 bytes) => 01 88 02 01 12 9e
>                1.052085     read: (8 bytes) => 01 88 04 01 12 00 00 a0
>                1.052211     send: (6 bytes) => 01 88 02 01 13 9f
>                1.116147     read: (8 bytes) => 01 88 04 01 13 31 49 1b
>                1.116283     send: (6 bytes) => 01 88 02 01 14 a0
>                1.180087     read: (8 bytes) => 01 88 04 01 14 30 37 09
>                1.180210     send: (6 bytes) => 01 88 02 01 15 a1
>                1.263082     read: (8 bytes) => 01 88 04 01 15 31 52 26
>                1.263205     send: (6 bytes) => 01 88 02 01 16 a2
>                1.329086     read: (8 bytes) => 01 88 04 01 16 30 35 09
>                1.329210     send: (6 bytes) => 01 88 02 01 17 a3
>                1.395086     read: (8 bytes) => 01 88 04 01 17 32 4d 24
>                1.395208     send: (6 bytes) => 01 88 02 01 18 a4
>                1.469080     read: (8 bytes) => 01 88 04 01 18 30 36 0c
>                1.469202     send: (6 bytes) => 01 88 02 01 19 a5
>                1.533086     read: (8 bytes) => 01 88 04 01 19 00 00 a7
>                1.533209     send: (6 bytes) => 01 88 02 01 1a a6
>                1.597114     read: (8 bytes) => 01 88 04 01 1a 00 00 a8
>                1.597239     send: (6 bytes) => 01 88 02 01 1b a7
>                1.662085     read: truncated: (5 bytes) => 01 37 01 04 3d
>                1.662194     GTX2 capable UPS not detected
> 
> 
> 
>             On Tue, Apr 6, 2010 at 4:32 PM, Richard Gregory
>             <R.Gregory at liverpool.ac.uk
>             <mailto:R.Gregory at liverpool.ac.uk>> wrote:
> 
>                 Hi All,
> 
>                 There were other byte swap issues with the driver,
>                 making all the bit field flags wrong. Have swapped them
>                 and can confirm the OL, OB and CHRG flags work. CHaRGing
>                 is not the inverse of Liebert's BATTERY_CHARGED flag as
>                 that means CHRG is set when the UPS is on battery. Is it
>                 reasonable to correct for this by ANDing with the OL flag?
> 
>                 Byte swapping patch attached.
> 
> 
>                 Richard
> 
>                 +--                               --+
>                 |  Biological Sciences, Room 231    |
>                 |  http://www.csc.liv.ac.uk/~greg
>                 <http://www.csc.liv.ac.uk/%7Egreg>   |
>                 +--                               --+
> 
>                 Arjen de Korte wrote:
> 
>                     Citeren Robert Jobbagy <jobbagy.robert at gmail.com
>                     <mailto:jobbagy.robert at gmail.com>>:
> 
>                         The trouble  was in the command reply buffer use.
>                         You compute the value that value =
>                         reply[6]*256+reply[5]  <- it's wrong
> 
>                         The right solution: value = reply[5] * 256 +
>                         reply[6];
> 
> 
>                     Thanks for this patch. I just committed it to the
>                     development version.  But please note that this is
>                     an experimental driver. Most of the  functions are
>                     untested (since nobody took the time to try it out
>                     and  post the results back to the mailing list).
> 
>                         And other bug,
> 
>                         battery.runtime compute, you divide this value
>                         60 <- it's wrong
> 
>                         right value: divide 1.0
> 
> 
>                     Probably not. Per the NUT standard, the
>                     'battery.runtime' value is  reported in seconds. As
>                     far as I understand, the UPS reports runtime
>                      remaining in minutes, so we need to multiply by 60
>                     here. See  'docs/new-names.txt' for a listing of
>                     (almost) all variables supported  in NUT.
> 
>                         I continue the work on this driver,and I will
>                         write if I make a something
>                         new.
> 
> 
>                     Please do. It should be trivial to add additional
>                     commands and  variables to the existing ones.
> 
>                     Best regards, Arjen
> 
> 
>                 _______________________________________________
>                 Nut-upsdev mailing list
>                 Nut-upsdev at lists.alioth.debian.org
>                 <mailto:Nut-upsdev at lists.alioth.debian.org>
>                 http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev
> 
> 
> 
> 
>         _______________________________________________
>         Nut-upsdev mailing list
>         Nut-upsdev at lists.alioth.debian.org
>         <mailto:Nut-upsdev at lists.alioth.debian.org>
>         http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev
> 
> 
> 
> 
>     -- 
>     Best Regards,
> 
>     Robert
> 
> 
> 
>     -- 
>     Best Regards,
> 