[Nut-upsdev] Syslog flooding

Arjen de Korte nut+devel at de-korte.org
Tue Apr 20 07:29:42 UTC 2010


Citeren Kelvin Ku <kelvin op telemetry-investments.com>:

> When I restart NUT, everything is OK until the next spontaneous  
> reconnection. Two questions:
>
> 1. If I can reset the connection by restarting the driver, is there a way to
> make the driver do this itself?
>
> 2. If not, is there a way to suppress or limit the syslog messages,  
> other than
> a syslog filter?
>
> Note that I have three other UPSs of the same type which do not exhibit this
> behavior.

If you're monitoring two (or more) UPSes from the same host system,  
make sure they can be uniquely identified by the regular expressions  
you specified in 'ups.conf'. The situation you're describing is  
typical for an installation where this is not done properly (see also  
'man 8 usbhid-ups'). The regular expressions are *mandatory* as soon  
as you connect multiple UPS devices to a single host.

Best regards, Arjen
-- 
Please keep list traffic on the list




More information about the Nut-upsdev mailing list